Should a fire alarm system be installed in the factory control room?

2016-04-27View Original

Thread Content

I have a question for everyone. We are a chemical plant, with personnel in the control room 24 hours a day. After checking the relevant standards, I couldn’t find any clear indications as to whether it is necessary to install fire alarm systems. I would like to ask if there are any requirements regarding whether such systems should be installed or not.
Reply #22016-04-27
It needs to be set up, and the alarms from the device should also be routed to the control room, as there is someone on duty 24/7 to detect them easily.
Reply #32016-04-27
Could you tell me which standard states that? I couldn’t find any information on this one
Reply #42016-04-27
Basis: GB 50116 - 2013 Code for Design of Automatic Fire Alarm Systems. 3.2.2 The design of a zone alarm system shall comply with the following provisions: 1 The system shall consist of fire detectors, manual fire alarm buttons, fire sound and light alarms, and fire alarm controllers; it may also include a graphic display device in the fire control room as well as zone displays indicating the floors. 2 The fire alarm controller should be installed in a location where there is someone on duty. It can be seen that it doesn’t necessarily have to be located in the control room, but generally companies place it there ; Because there are people working here 24 hours a day ; Of course, there are also many companies that have their security rooms set up in such locations ;
Reply #52016-04-27
Upstairs, that standard is set by the fire alarm controller
Reply #62016-04-28
We also experienced a false alarm during the setup process; there were flies in the control room, so insecticide was sprayed, and accidentally it got on the sensor. This caused an alarm in the middle of the night, and the factory’s fire team was ready to come over. Fortunately, we were able to get in touch in time and cancel the false alarm~~~
Reply #72016-04-28
The control room must be equipped with fire safety measures, and employees must complete fire emergency training and pass it before they can take up their posts. The control room is crucial for the overall safety of the production area.
Reply #82016-04-28
At least clarify what kind of factory it is and what the main materials used in its operations are. GB 50116 - 2013 Code for Design of Automatic Fire Alarm Systems, Article 6.3.1: Each fire compartment shall be equipped with at least one manual fire alarm button. The walking distance from any location within a fire compartment to the nearest manual fire alarm button should not exceed 30 m. Manual fire alarm buttons should be installed in evacuation passages or at exits.
Reply #92016-04-28
Code for Fire Protection Design of Petrochemical Enterprises GB50160-2015, Article 8.12.1; It must be set; if not, you’ll have to wait for the safety inspection authorities to fine you, and you won’t be able to pass the safety assessment either.
Reply #102016-04-28
Coal chemical industry, phosphate chemical industry – there are issues with all of them, so it’s difficult to know how to deal with them.
Reply #112016-04-28
1. What’s difficult about it? Large companies in the coal chemical industry have professional designs; just find the \"Preliminary Design and Safety Section\" to take a look, and everything will become clear. 2. Refer to Chapter 8.4 of the Building Design Fire Protection Code; installation is required if the conditions are met. 3. Paragraph 6 of Article 4.1.13 of the “Code for Safety and Health Design of Chemical Enterprises” (HG20571-2014): “Automatic fire alarm systems shall be installed in key chemical production units, control rooms, substation areas, warehouses storing flammable materials, and oil depots.” The design of the automatic fire alarm system shall meet the requirements of the current **standard, the “Code for Design of Automatic Fire Alarm Systems” GB50116.

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.