The heights of the isolation tanks for orifice plate flowmeters are not consistent

2016-07-29View Original

Thread Content

What impact does an excessively high negative pressure in the isolation tank of a orifice plate flow meter have on differential pressure measurement? High or low? Gentle experts, could anyone help me answer this?
Reply #22016-07-29
A high negative pressure on the isolation tank side will result in a reduced differential pressure, which in turn leads to lower measurement values
Reply #32016-07-29
It shall meet the requirements of GB 50093-2013 \"Code for Construction and Quality Acceptance of Automatic Instrumentation Projects\".
Reply #42016-07-29
When the pressure on the positive side is high, the differential pressure increases, resulting in higher measurement values; when the pressure on the negative side is high, the differential pressure decreases, leading to lower measurement values. Generally, if the installation heights are not consistent, it is necessary to make adjustments. In addition to differences in installation height, varying liquid levels inside the tank can also affect the measurement values
Reply #52016-07-29
The installation height generally cannot be exactly the same, nor can the liquid level inside the tank be exactly at the same level. Therefore, it is advisable to perform a calibration before putting the flow meter into use in order to eliminate the effects of such differences.
Reply #62016-07-29
Thank you very much. Is there any difference if I just set it to zero instead of migrating it?
Reply #72016-07-29
This post was last edited by cqdfwy on 2016-7-29 at 11:56. It depends on the specific details of the differential pressure transmitter you are using; zeroing it can be done as long as the transmitter’s range is not changed (here, this does not refer to the upper measurement limit, but rather to the value between the upper and lower measurement limits). Modern smart transmitters no longer have separate zero-point adjustment mechanisms; zero adjustment is used instead.
Reply #82016-07-29
It has an impact; the differential pressure value will be lower than the actual value.....

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.