Can the DCS range be set from -10 KPA to 10 KPA, with the set point at 0?
Reply #22016-07-29
The settings in the DCS must be consistent with those of the transmitter unit; if the input pressure of the transmitter is -10kPa to 10kPa, then the settings in the DCS should also be -10kPa to 10kPa.
Reply #32016-08-01
It is not uncommon for the range to not be 0; all DCS systems support this. Additionally, DCS systems are generally designed to be comprehensive in their functionality – for example, it is possible to set them to operate in reverse mode, such that 4-20mA corresponds to pressures ranging from +10Pa to -10kPa

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.