Issues regarding MTL and DCS serial communication

2016-08-07View Original

Thread Content

In our factory, the acquisition and display of temperature signals from a certain device are carried out through an MTL838B-MBF multi-channel temperature converter, which communicates via serial port with the ECS-700 COM741 card produced by Zhejiang University’s Control Systems Department. Recently, we have observed an irregular tendency for the communication data to return to zero. I would like to ask the experts here: what could be the cause of this issue?
Reply #22016-08-07
After changing the hardware baud rate of the MTL multi-channel temperature converter and the internal baud rate in the DCS communication configuration from 9600 to 19200, the display worked properly. Could everyone analyze the reasons?

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.