Is an isolator needed if the transmitter is too far away from the DCS room?

2016-09-17View Original

Thread Content

The field pressure transmitter is 1 kilometer away from the control room; it uses shielded cables. Is there much signal attenuation for a 4-20 ma signal? Is it necessary to use an isolator or any other form of compensation?
Reply #22016-09-17
How many channel signals can a cable generally support without interference between them?
Reply #32016-09-18
The voltage drop across the cable must ensure that the field transmitter can operate properly; otherwise, the cross-sectional area of the cable should be increased.
Reply #42016-09-18
For wire diameters greater than 1,5 mm2, 1 km is no problem.
Reply #52016-09-18
One kilometer isn’t a long distance; the key is that the resistance value of the instrument cable must be within the specified range – if it isn’t, even a few hundred meters won’t suffice

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.