There is a problem with setting the average thermometer on the NRF590

2016-09-21View Original

Thread Content

I have two tanks here, G1302 and G1306, both of which use average temperature probes. When the element type set for the temperature indicator next to the tank is PT100, the temperature reading is 20 degrees too low; when PTCU100 is set, the temperature display is normal, with the lowest reading showing 999 degrees. Moreover, the NRF590s next to the cans are all new. What is the reason for this?
Reply #22016-10-05
Is the average thermometer also from E+H? Based on the symptoms, could it be an error caused by inaccurate insertion depth settings of the average temperature meter?

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.