Distance requirements between LNG storage tanks and buried oil pipelines

2016-10-25View Original

Thread Content

I would like to ask the experts: what is the safe distance between LNG storage tanks and buried oil pipelines? I couldn’t find this information in any standards.
Reply #22016-11-12
GB50183 does not have a direct one. 1. Reference can be made to Table 4.1.9 of GB50160; for LNG storage tanks, the provisions applicable to liquefied hydrocarbon storage tanks shall be used, with a distance of 30 meters from the oil transfer pipelines. However, note clause 4.1.8: regional oil (gas) pipelines should not pass through the plant area. 2. Refer to the Design Code for Natural Gas Liquefaction Plants (draft for comments) prepared by Editor-in-Chief Guo of Shaanxi Fuel Research Institute; Table 4.0.6 specifies that the distance between the LNG storage tank and the regional flammable liquid storage tanks should be 50 m.

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.