The Romon dual-flange differential pressure transmitter on site indicated an overrange of 485%

2016-12-09View Original

Thread Content

This post was last edited by haoliu8733 on 2016-12-9 at 21:58. The Romon double-flange differential pressure transmitter shows an overload value of 485%; the ambient temperature indicated on the gauge is -40 degrees. Does this not refer to the temperature of the silicone oil? It measures the liquid level in a three-phase separator; the fluids involved are natural gas, water, and heavy hydrocarbons. In this separator, the bottom layer is water, while the middle layer consists of heavy hydrocarbons. This gauge is used to measure the liquid level of the heavy hydrocarbons. The operating temperature of the storage tank is -15 degrees. Could it be that the diaphragm box has frozen? Is it blocked again? How can one determine whether the problem lies with the flange diaphragm box, or with the capillary tube or gauge head? I would appreciate some advice from everyone.
Reply #22016-12-10
It’s best to check the instructions; they can be found online
Reply #32016-12-10
40 refers to the ambient temperature of the transmitter body; silicone oil cannot reach such low temperatures. To achieve -15 degrees Celsius, insulation materials must be used around the capillary, and the same applies to the flange area, otherwise the measurement results will be inaccurate
Reply #42016-12-16
Double flanges seem to give quite inaccurate readings for this type of measurement......
Reply #52016-12-16
It's very simple. This is because ice forms on the water side, and the expansion of the ice exerts pressure on the diaphragm box, resulting in high pressure. Just blow on the pressure tapping with steam. It would be better to remove and clean it after closing the root valve.

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.