Verification of the safety valve after parking

2018-01-30View Original

Thread Content

Shut down the unit, remove all safety valves and take them for calibration. What specifically needs to be verified? How to test it? I’d like to ask everyone!
Reply #22018-01-30
First, verify the launch pressure, check the sensitivity, and apply seals, etc
Reply #32018-01-30
Safety valves must be calibrated annually. The procedures include: 1. Purging to remove dust; 2. Calibrating the opening pressure PS; 3. Checking the return pressure and performing a seal test; 4. Applying lead seals and installing labels; 5. Adjusting PS via springs. In the event of internal leakage, the valve needs to be ground and repaired or replaced
Reply #42018-01-30
It mainly involves checking the opening and closing pressure, and this is usually carried out by the quality control department
Reply #52018-01-30
The main task is to verify whether the operating pressure meets the required standard; if the operating pressure is not correct, the internal spring needs to be adjusted
Reply #62018-01-30
The main tasks are to check whether the set pressure is appropriate, in order to avoid situations where the device fails to activate when it should, or activates when it shouldn’t. Additionally, it is necessary to examine the sealing condition, as well as whether the springs are broken or clogged.
Reply #72018-02-03
This post was last edited by w1d3d55 on 2018-2-3 at 11:00 in accordance with the Safety Technical Inspection Regulations for Safety Valves (TSGZF001)

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.