For material tanks equipped with nitrogen sealing and flame arrestor vent valves, what should be the appropriate opening pressure for these vent valves?

2019-06-16View Original

Thread Content

For atmospheric pressure material tanks equipped with nitrogen blanketing and flame arrestor vent valves, what is an appropriate setting for the opening pressure of these vent valves?
Reply #22019-06-16
The pressure of the flame arrestor breather valve is probably around 1500 Pa higher than that of the nitrogen seal valve; it depends on the design
Reply #32019-08-16
It is determined by estimating the design pressure of the storage tank! Taking a storage tank with a design pressure of 2 KPA as an example, the nitrogen seal is set at 200–500 Pa, the single vent valve is set at 900 Pa, and the breather valve is set at 1300 Pa!

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.