Pipeline static grounding

2019-06-16View Original

Thread Content

The pipes within the plant are installed on steel pipe racks; is it still necessary to provide separate electrostatic grounding for these pipes? If it is concrete, how should static grounding be carried out? Are there any picture albums I can refer to?
Reply #22019-06-16
Static bonding of pipeline flanges and static grounding of pipe racks are sufficient
Reply #32019-06-17
Generally, pipelines nowadays need to be electrically grounded every 50 to 80 meters. For steel pipe racks, jumper wires are required to connect them to the pipe gallery; for concrete pipe galleries, wires must be led to underground electrodes. If you need sample diagrams, feel free to message me privately
Reply #42020-05-14
I found your reply post; I have these same doubts now. Could you also send me a sample image? jack5885@126.com. I am extremely grateful.

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.