8.2 MPa, steam valve at 350 degrees – what material is suitable for the valve internals, and which standards should be referred to?

2019-10-09View Original

Thread Content

As the title suggests, could experts please recommend some materials as well as relevant standards or information? Thank you all. By the way, is it okay to use 17-4PH for the valve internals?
Reply #22019-10-10
When used in accordance with ASME specification 17-4PH, the temperature must not exceed 343°C. What type of valve have you chosen for this steam medium?
Reply #32019-10-10
This post was last edited by chuane on 2019-10-10 09:30. It is recommended to consult the Practical Design Manual for Valves, edited by Lu Peiwen. You also didn’t specify the type of valve you need or its purpose; how can I give you advice then? Is it meant for regulating flow or for shutting off or redirecting flow? . . :)
Reply #42019-10-10
The valve type is a multi-stage pressure-reducing cage valve, used for regulation
Reply #52019-10-10
Firstly, is this valve intended for regulation or just on/off control? A three-eccentric valve should work for on/off control, and a ball valve is also an option. For regulation purposes, a globe valve is suitable; for valves operating at 350°C, 316HT or some material with better heat resistance may be required for the internal components.
Reply #62019-10-10
I checked the design manual; it only mentions a temperature of 400 degrees, with no information on pressure
Reply #72019-10-10
For control valves, it is recommended to determine the appropriate design temperature carefully; if it is below 343°C, 17-4PH could be considered, while if it is above 343°C, other materials might be suitable

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.