For a pressure range of -100~0 KPa, does it correspond to 4~20 mA or 20~4 mA?

2020-09-01View Original

Thread Content

The crude tower used for distillation is a vacuum tower, with a pressure range of -100 to 0 KPa. Does this correspond to a current range of 4–20 mA, or 20–4 mA? Or does it not matter which range is used, as long as the field instruments are matched with the DCS? Is that enough? For example, a field transmitter with a range of 100~0 KPa corresponds to 4~20 mA; the DCS configuration also uses 100~0 KPa, with a corresponding output of 4~20 mA. If the on-site pressure range is -100~0 KPa, which corresponds to 20~4 mA, and the DCS configuration also sets it at -100~0 KPa with a corresponding range of 20~4 mA, will that work?
Reply #22020-09-02
For 4 to 20 milliamps, pressure transducers generally output 4 to 20 milliamps, while DCs usually use the default value, which is also 4 to 20 milliamps
Reply #32020-10-28
4mA corresponds to the zero point of the measurement, not true zero; the zero point in the range of -100 to 0 refers to -100, so the corresponding current signal is 4-20mA

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.