KOSO Compatible Fisher 3800 Series Positioner Calibration Method

2020-11-24View Original

Thread Content

Fisher 3800 series locator 1: Press the up, down, left, and right buttons simultaneously to switch to Chinese. 2. Detailed settings: Power-off state —– (Valve open / Valve closed)
3. Press ▶ to change the pressure unit to —– KPA
4. Press ▶ to set the lower limit of the input range to —– 4.0mA
5. Press ▶ to set the upper limit of the input range to —– 20mA
6. Press ▶ to select the input characteristic as —– Linear
7. Press ▶ to set the transmitter output at full stroke to —– 4.0mA (valve closed)
8. Press ▶ to save and exit; a message will appear stating (Press ▶ for 3 seconds to activate the valve)
9. Press ▶ to enter stroke calibration ➡ Automatic; a message will appear stating (Press ▶ for 3 seconds, and the valve will move to start automatic scanning)

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.