Does the steam fire protection pipeline of the cooling tower originate from the main steam pipe?

2021-06-01View Original

Thread Content

The steam fire protection pipeline of the cooling tower can be led to the ground with a purging connection, from which it can be connected to a nearby hose station when needed. rather than being drawn from the steam main. Is it okay to do this?
Reply #22021-06-02
It is not recommended; Article 8.8.2 of GB50160 explicitly requires that fire-fighting steam should be introduced from the top of the main pipe. Imagine that in an emergency, if the personnel on the tower platform need to use steam to extinguish a fire, they have to go to the ground first to connect the hoses – this certainly poses operational risks.

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.