2022-02-28View Original

Thread Content

It is known that both the pressure before and after the valve is less than 16 kilograms; therefore, a valve with a design pressure of 16 kilograms is selected for use. Is it still necessary to know the specific pressures before and after the valve?
Reply #22022-02-28
Yes, it is necessary to provide as detailed parameters as possible for the control valve
Reply #32022-02-28
The working pressure is less than 16 kilograms; it could also be 15.999999 kilograms. The design pressure for the valve is set at 16 kilograms – don’t you think that’s too low? Is there no fluctuation at all in this system? Saving that much money?
Reply #42022-02-28
Control valves require upstream and downstream pressures as well as pressure difference; they also need flow rate information, specifications regarding noise level, flow speed limits, and valve structure.
Reply #52022-02-28
No, basically the pressure is always below 10 kilograms. The teacher in charge of the process package isn’t sure about the pressure before and after the valve, so he wants to know if it’s okay to use the design pressure of 16 kilograms
Reply #62022-03-03
Control valves are generally designed with a pressure rating one level higher; for your case, you should choose at least 2.5 MPa, or alternatively 4 MPa
Reply #72022-03-07
One thing to keep in mind is to prevent unexpected operating conditions from occurring; for example, the water hammer pressure generated by rapid opening and closing of valves can be much higher than normal pressure

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.