Why is the interlock setting for low liquid levels set so high?

2020-04-23View Original

Thread Content

Why are the interlocks for low liquid levels in several of the absorption pump chambers all above 20, while the low liquid level in the flue gas desulfurization tower is over 30? Experts, what is the reasoning behind setting such high values for the low liquid level? Generally, it’s 10 for low low and 90 for high high. ( 0 x 0 )
Reply #22020-04-23
Based on the normal operating flow rate and the volume of liquid stored in the tank, the time required to empty it can be determined, allowing sufficient time for processing and to set up alarms
Reply #32020-04-23
If it’s too low, it constitutes discrimination; the pressure of the pump is unstable, mainly due to the time required for fluid discharge
Reply #42020-04-30
Meet the requirements for the net positive suction head of the centrifugal pump
Reply #52020-05-02
Some have a high circulation flow rate and small tanks. Reaction time needs to be allowed to prevent cavitation
Reply #62020-05-05
It should be able to avoid cavitation for a certain period of time

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.