【Daily Question】Utilities - Water Supply and Drainage - 20191222

2019-12-22View Original

Thread Content

A certain underground garage is equipped with a pre-action automatic sprinkler system, and it has 1,388 sprinklers in total; therefore, this building requires (  ) alarm valves.       A.1       B.2        C.3         D.4  Answer: B is the correct answer. According to Article 6.2.3 of the current Code for Design of Automatic Sprinkler Systems, the number of sprinklers controlled by one alarm valve assembly in a pre-action system should not exceed 800. In this case, there are 1,388 sprinklers, and since a pre-action system is to be used, option B is chosen.
Reply #22019-12-22
B. According to Article 6.2.3 of GB 500841 \"Code for Fire Protection Design of Automatic Sprinkler Systems\", the number of sprinklers controlled by one alarm valve assembly in a pre-action system should not exceed 800. In this case, there are 1388 sprinklers, so option B is correct.

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.