DCS flow display

2021-06-19View Original

Thread Content

For gases such as hydrogen, if the flow rate is shown as 15000 Nm3/h, this value is already in standard conditions. If one wants to calculate the mass flow rate, then it is necessary to multiply by the density at standard conditions, right? Furthermore, if the actual hydrogen pressure (gauge pressure) is 2.0 Mpa, according to the ideal gas law, the actual density is nearly 20 times greater than that at standard conditions; in other words, the actual volumetric flow rate is 15000/20, which equals 750 m3/h. Is this understanding correct?
Reply #22021-06-23
It’s 21 times, not 20; everything else is fine. If you want greater accuracy, use the virial equation for calculation

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.