After the GB51142 standard was issued, how does sequential control function?

2017-04-25View Original

Thread Content

Hello everyone. According to Chapter 12 of the new standard, the \"Design Code for Liquefied Petroleum Gas Supply Engineering\" GB51142-2015, it states that \"combustible gas alarm controllers should be interlocked with the control system.\" I would like to ask how people implement this interlocking when working on such projects? ? Does a concentration alarm in a specific area cause the inlet and outlet valves of that area to be closed? ?
Reply #22017-04-25
When the combustible gas level in the process unit area exceeds the limit, the station shutdown is triggered, and the inlet and outlet isolation valves are shut off via interlock.

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.