Heating furnace blower renovation

2019-03-01View Original

Thread Content

The actual load of the heating furnace is **lower than the designed load; therefore, even when the frequency of the blower is set at its lowest level, it is still necessary to use the inlet damper for control. However, closing the inlet damper too much results in large fluctuations. Are there any alternative methods to reduce the blower’s power output, apart from adjusting its frequency? Also, the magnetic coupler and the frequency converter should be the same, right? I hope the experts can give some advice!
Reply #22019-03-05
A hydraulic coupling is also used to reduce speed, but its adjustment range is not as wide as that of an inverter, so it is not suitable for your application conditions. Your actual operating conditions are much worse than the designed ones; there are better ways to make improvements. I’ve sent you a message – add me on WeChat

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.