On axial flow compressor control

2021-07-13View Original

Thread Content

As shown in the figure, the pressure difference at the throat of the axial flow compressor is used in the anti-surge control of the compressor; why is BIC used to represent it in the figure? Instead of FIC? Is there any indication of backflow protection in the diagram?
Reply #22021-07-14
Centrifugal anti-surge control includes flow control and outlet pressure control. In axial flow systems, surge is generally caused by high outlet pressure; controlling the vent valve can prevent this phenomenon. The input value for BIC is the pressure difference at the throat, along with an adjustment for the inlet temperature. These values are used in calculations to determine the maximum allowable discharge pressure, which is then compared with the current discharge pressure to calculate the MV value, thereby controlling the opening degree of the vent valve. Then why use throat pressure difference as the control variable? Since this variable has a functional relationship with the exhaust pressure, it actually also has a functional relationship with the flow rate. In fact, all of them use throat pressure differences, probably to facilitate calculation or to enable anti-stall control
Reply #32021-07-14
Engineer Luan, if you encounter any difficulties with the new project, feel free to post more requests for help here. Everyone can help you discuss it together. Wish you success soon!
Reply #42021-07-14
The conditions for surge are nothing other than low flow rate and high pressure ratio; The stationary vanes of axial flow compressors generally have a minimum opening angle that cannot be reduced to 0. The throat differential pressure makes it easier to calculate the operating point, providing an intuitive indication compared to the anti-surge line; in other words, as mentioned on the second floor, this facilitates surge control
Reply #52021-07-15
:Hug: I studied Shaanxi Blower’s control system a little yesterday, and found that its throat pressure difference feature includes detection functions for surge protection and backflow prevention. Backflow occurs when there is a sudden increase in pressure in the downstream system, as a result of further surge conditions or failures in the process system.
Reply #62021-07-17
Now, Shaanxi Blower also adds an alarm for the blockage curve
Reply #72021-07-17
The flow rate is indicated by the pressure difference in the throat, rather than the actual flow rate measured by the flow rate sensor

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.