2017-10-01View Original

Thread Content

Recently, our single-flange level gauges have been showing inaccurate readings frequently. After having the instrumentation control team calibrate them, the readings were off again after another calibration attempt. The medium being measured is a liquid that is acidic and contains flocculent substances. The level gauge was recalibrated, and no issues were found with the instrument, but this phenomenon cannot be resolved. I would like to ask the experts here – do you have any suggestions or insights that could help broaden my horizons?
Reply #22017-10-01
Our company has encountered issues with single-flange level gauges giving inaccurate readings; the reason for this was that the exhaust pipe on the atmospheric side of the transmitter had been blocked by bees, which built nests there. Second, the large air duct for maintaining balance in the storage tank is too small; when a large amount of material is introduced into the tank, exhaust is not carried out in a timely manner, resulting in inaccuracies in the short term.
Reply #32017-10-01
First, check whether there is any blockage at the flange connection. If there is no blockage, consider replacing the transmitter; it’s likely that the transmitter’s performance is poor and its readings drift significantly.

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.