A valve is installed between the safety valve and the silencer; which requirement is not met?

2018-04-25View Original

Thread Content

Today, an external inspection was carried out on an industrial boiler (steam boiler), and it was found that a valve had been installed between the safety valve and the silencer (note: at the outlet of the safety valve). It is generally considered that this violates the regulations; I would like to ask gently – does this violate the provisions of the boiler regulations regarding the installation of safety valves?
Reply #22018-04-25
No valves shall be installed at the outlet of the safety valve.
Reply #32018-04-26
It is not advisable to install a stop valve between the safety valve and the container
Reply #42018-04-26
There is no mandatory prohibition on installation; only a seal needs to be applied
Reply #52018-04-26
It is stipulated in TSG ZF001-2006 Regulations on Safety Technical Inspection of Safety Valves
Reply #62018-04-26
This post was last edited by zjq1962 on 2018-4-26 at 10:36. It can be installed, but the impact of the muffler on back pressure after installation must be taken into account.
Reply #72018-04-26
No valves can be installed downstream of a safety valve; it’s quite easy to understand – if a valve is installed after the safety valve and that valve happens to close, the safety valve will no longer be able to perform its function of releasing pressure
Reply #82018-04-28
The outlet of the boiler’s safety valve usually leads directly to the atmosphere; installing a valve there serves no purpose at all. So why install it? Is it just out of mere extravagance?
Reply #92018-04-28
It should be possible to install it, but a lead seal must be added and the stop valve must remain fully open.
Reply #102019-01-07
Violation of clause 11.1.5 of DL5054

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.