2018-12-17View Original

Thread Content

Dear experts in the marine field: I have a question. The wind bending moment calculated by the software is 10,000. Why is it necessary to multiply this value by a factor of 1.4 when specifying the foundation conditions, resulting in 14,000? Which standard specifies this factor? Thank you!
Reply #22018-12-17
1.4 is the wind load partial factor
Reply #32018-12-18
What was said upstairs is correct; you can refer to the provisions regarding the partial coefficients for variable loads in clause 3.2.4 of the standard GB50009-2012.

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.