The heating temperature of the factory heating panel is not enough in winter. How to analyze the fault?

2022-07-26View Original

Thread Content

Please ask experts, how to analyze the picture data to find out that the primary side medium flow is insufficient. This fault can be solved by increasing the flow rate of the heat source or increasing the diameter of the heat source medium pipeline.
Reply #22022-07-26
Because the return water temperature of the primary network and the water supply temperature of the secondary side are 1.8 degrees, it means that the heat exchange is sufficient. Therefore, the water supply temperature of the secondary network does not meet the requirements because the flow rate of the primary network is insufficient.

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.