Issues regarding the classification of fire hazards in industrial buildings

2017-10-23View Original

Thread Content

There is a nitrogen compressor room; the facility contains only two nitrogen compressors with a capacity of 150 NM3/H each. These two compressors account for approximately 50% of the floor space. The nitrogen gas contains 3%-4% methane (the lower explosive limit for methane is 5%). Is this facility considered a Class A facility? What should I do?
Reply #22017-10-23
There is already an explosion lower limit that meets Class A requirements
Reply #32017-10-24
It is not classified as Category A; this can be seen from the explanatory notes to Article 3.1.2 of the Building Code.

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.