Fire separation distance in tank farm area

2020-09-10View Original

Thread Content

I would like to ask fellow sailors: should the fire separation distance between Class A tank areas and other buildings be measured from the outer wall of the tanks, or from the fire dike?
Reply #22020-09-10
See attached figure, GB50160
Reply #32020-09-11
The outer wall of the tank is mentioned in the interpretations of petrochemical regulations.
Reply #42020-09-11
This is definitely calculated based on the outer wall of the tank; both the Building Design Fire Protection Code and the petrochemical regulations specify this
Reply #52020-09-11
Measured from the outer wall of the storage tank, but the fire dike must be at least 10 meters away from adjacent buildings. See the notes in the Building Code.

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.