Help: For the 4211 valve, when the feedback indicates an intermediate opening degree of 12 mA, the actual value is 12.7 mA, which is inaccurate; after 12 mA, the difference is usually around 0.5 mA. (Both the zero point and full stroke are accurate, with a difference of 0.15mA)
Reply #22017-02-13
For something like this, basically all that’s needed is to calibrate the zero point and the range; of course, this assumes good linearity. If the linearity is poor, it’s usually a problem with the potentiometer
Reply #32017-02-13
Valve position transmitters give inaccurate feedback; the factory had already pointed out that it’s better to use Siemens’ valve position feedback module.
Reply #42017-03-06
I haven’t used it; can it be used to verify linearity?

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.