Is it necessary to take the square root when using an online differential pressure transmitter for boiler air and powder to measure wind speed?

2017-02-16View Original

Thread Content

Dear teachers, regarding the online measurement of the air velocity in the powder tube of the boiler’s air-powder system (in m/s), a differential pressure transmitter is used for this purpose. Is it necessary to perform a square root calculation on the data from the transmitter or the DCS?
Reply #22017-02-17
In a differential pressure flow meter, there is a square root relationship between the differential pressure and the flow rate.
Reply #32017-02-17
It is usually a pitot tube flow meter, and the differential pressure value requires square root calculation.
Reply #42017-02-17
For the flowmeter in the differential pressure throttling device, the signal needs to be squared; either a DCS or a transmitter can be used, one of the two.
Reply #52017-02-17
Only one of the transmitter or the DCS needs to have its value taken to the square root; it is not possible to take the square root of both the transmitter and the DCS.

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.