Transmission distance of frequency signals?

2017-02-24View Original

Thread Content

Field vortex flow meters, or speed measurement devices, both output voltage-frequency signals. How far can these signals generally be transmitted?
Reply #22017-02-25
Use twisted pair, or even dedicated cables. If the interference is low, several kilometers is possible
Reply #32017-02-28
Generally speaking, the absolute transmission distance can be guaranteed, but the signal-to-noise ratio cannot be generalized; therefore, the effective transmission distance varies. Different signal frequencies (wavelengths) require different electromagnetic shielding methods, and incorrect grounding of the shielding wires directly affects the quality and range of signal transmission. It is recommended to refer to certain parts of Section 6 of the IEEE Standard 1050 for analysis.

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.