The E+H electromagnetic flowmeter shows flow rate as soon as it is turned on

2017-03-19View Original

Thread Content

After installation, when it was turned on, a flow rate of 7 L/MIN was displayed; this value kept fluctuating, and no alarm was triggered; The flow meter is installed vertically; when I fill the pipe with water, the flow reading is 0, which is normal. Could it be due to an empty pipe? I have set the air management detection to ON STANDARD; there are alarms for low flow in the meter, but an alarm is still triggered when there is water in the pipeline. What’s going on? Is something not set correctly?
Reply #22017-03-19
Check whether the grounding is properly connected; if not, cut off the flow at a low level

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.