Problems with pressure transmitters measuring pulsating pressure

2017-06-07View Original

Thread Content

There is a project that requires measuring the pressure in the pump outlet pipeline. Could pressure fluctuations affect the selection of pressure transducers? If threaded installation is used, what additional accessories are needed? Is it feasible to use flange mounting? How far from the pump outlet can pulsation pressure be ignored? Thank you
Reply #22017-06-07
It should work! Pulsating pressure gauges also come with flanges
Reply #32017-06-07
Pump outlet --- pressure gauge ---- check valve ---- globe valve. This is the order of installation. For a single-flange pulse-type pressure transmitter, it is recommended to install it at a distance of 2-3 meters; if it is too close to the variable-frequency pump, there will be significant fluctuations, while if it is too far away, there will be considerable lag. Consider this carefully before making a decision.
Reply #42017-06-08
It is worth exploring and studying how far away from the pump outlet the pressure transmitter should be installed; I’ll go look for some information to learn more about it :P
Reply #52017-06-08
The pressure gauge really wears out very quickly
Reply #62017-06-08
Add buffer tanks or U-bends when necessary.
Reply #72017-06-09
For piston pumps, install the damping bend at a distance, preferably in a location where pressure fluctuations are minimal; for centrifugal pumps, they can be installed as usual!
Reply #82017-06-09
Add a damping screw; it’s best to use a stainless steel diaphragm

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.