Please ask the experts in the community to help analyze it! Due to **safety requirements, the device requires an SIS system. For the existing control valve, I want to add a solenoid valve to it for use in SIS control for emergency interlock shutdown. Whether it meets the requirements of the design specifications. Follow that standard. The system is required to meet the SIL2 level. Of course, it's better to add an independent cut-off valve. Please help to discuss and analyze this from a regulatory perspective.
Introduction to Explosion-Proof Emergency Shut-Off Valves: The explosion-proof emergency shut-off valve (hereinafter referred to as the shut-off valve) is a new type of emergency shut-off device that serves as a reliable and essential safeguard to prevent oil leaks in oil depots, as well as accidents such as oil spills, fires, and explosions in oil tanks. It plays a particularly important role in ensuring the safety of property and personnel. It can be connected to level gauges, combustible gas detectors, and other fire-related safety instruments; in the event of an accident at an oil depot or chemical plant, the shut-off valve will close quickly thanks to the alarm signals or an emergency power cut, thereby stopping the flow of oil or chemical liquids and preventing the accident from worsening. Application scope and uses of explosion-proof emergency shut-off valves: This product is suitable for the inlet and outlet pipelines of oil tanks in oil depots and chemical plants. In the event of spills or leaks of oil or chemical liquids, as well as in case of fires, the emergency shut-off valve can be activated to cut off the flow of such oils or hazardous chemicals. Reduce the occurrence of explosion and fire accidents caused by leaks, and ensure the safety of ** and the lives and property of the people.
According to Clause 7.2.2 of the standard GB/T 50770-2013 for SIL2-level safety instrumented functions, control valves should be separated from the basic process control system. The specifications do not require it to be set up independently. Therefore, doing this does not violate the regulations.
SIL2 is determined through calculation. If an electromagnetic valve is installed on the valve, it is possible to calculate that the requirements of SIL2 can be met; certainly, this is feasible. Based on past experience, installing an electromagnetic valve on a standalone control valve usually does not result in a SIL2 rating
The original control valve required SIL2 certification
There’s no need to discuss it; the regulations have clear requirements – go and check them yourself.
First of all, it is possible; adding a solenoid valve to the SIS poses no problem at all; Secondly, is the sealing grade of the valve sufficient? Generally, the control valves of GLOBE models come with a Class IV seal – and those are devices that still leak water even when tightly closed; it’s necessary to verify the seal rating ; Finally, it is necessary to check the response speed, to ensure that the solenoids are all turned off and that the valves can move to their positions properly.
I attended a training session led by a foreign expert; it seems that the highest level for control valves combined with solenoid valves is SIL1. Also, are you sure that the solenoid valve you are using is designed for independent protection, so that the system can still be protected in case this valve fails?
Sharp, hitting the mark exactly. I like your answer. :handshake
A HAZOP assessment is still necessary; the decision should be made based on your actual operating conditions. For example, in the process package for Casale, the outlet valve of its medium-pressure separator is designed in the way you mentioned. Under normal operating conditions, the DCS performs regulation; when interlock conditions are met, the SIS triggers the de-energization of the solenoid valve.
HG/T 21581-2012 contains numerous valve pneumatic circuit diagrams; it is recommended that the original poster take a look.