To read the number of forced points in the HIMA system (H51 series), is it necessary to use an intermediate variable?
Reply #22018-05-07
I checked the manual; this parameter is not available in the system variables – there are only BOOL status values such as Force switches outputs/inputs and Master force outputs/inputs. It can be seen in the pop-up panel for the force switch under the control panel interface
Reply #32018-05-09
I consulted an HIMA engineer; by adding a UINT (unsigned integer) variable and connecting it to the internal variable for the force value through HIMA’s HW assignment, this can be achieved.

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.