Does the transmitter show flow rate when there is backflow in the orifice plate flow meter?

2017-06-20View Original

Thread Content

As the title says, waiting online, thanks! !
Reply #22017-06-20
Yes, it’s just that the data volume shown is on the low side.
Reply #32017-06-20
The transmitter shows 0, and it also displays an error message. Thank you!
Reply #42017-06-20
The transmitter shows 0, and it also displays an error message. Thank you!
Reply #52017-06-21
The differential pressure transmitter detects a negative differential pressure, which is outside the lower limit of the measurement range. Typically, the lower limit value of 0 kPa is displayed; when converted to a percentage, this becomes 0, and after taking the square root it is also 0. Therefore, the actual indicated value is also 0
Reply #62017-06-21
The traffic volume is incorrect, but there is some traffic, just a low amount.

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.