I’ve only recently started working with Emerson DELTAVIS SIS, and my knowledge of it is limited. The original logic controller in the factory’s DELTAVIS SIS system, an SLS 1508, indicated a fault. I replaced it with a spare unit. The indicator lights on the new logic controller – lights 1 and 2, as well as lights 3 and 4 – flickered alternately for about a minute, after which light 1 remained on constantly while light 4 continued to flicker. There was no display on the system either. What could be the cause of this? I need someone who knows DLETAV SIS to help answer this.
SLS 1508 is generally configured in a redundant manner. After you replace it, lights 1 and 2, as well as lights 3 and 4, will flash alternately every minute, as the module undergoes power-on self-check. After that, 1 light remains on continuously while 4 lights flash. The official explanation is: it is in use, not configured, or being configured. It seems that the new one is synchronizing with the ACTIVE SLS 1508; once the synchronization is complete, everything should be fine. It will be normal once 1 and 4 are constantly lit.
So if it’s always in sync, how should it be handled to make it work properly?
Similar to DCS systems, after replacing the control cards in a SIS system, it is necessary to upload the existing configuration program; If the 4 lights keep flashing, it indicates that the configuration program was not installed successfully; it’s possible that the system does not support automatic installation, and manual setup is required ; It is also possible that there have been changes in the logic settings, requiring reconfiguration.
Similar to DCS systems, after replacing the control cards in a SIS system, it is necessary to upload the existing configuration program; If the 4 lights keep flashing, it indicates that the configuration program was not installed successfully; it’s possible that the system does not support automatic installation, and manual setup is required ; It is also possible that there have been changes in the logic settings, requiring reconfiguration.
Similar to DCS systems, after replacing the control cards in a SIS system, it is necessary to upload the existing configuration program; If the 4 lights keep flashing, it indicates that the configuration program was not installed successfully; it’s possible that the system does not support automatic installation, and manual setup is required ; It is also possible that there have been changes in the logic settings, requiring reconfiguration.
If the SIS card is removed and then reinstalled, it needs to be downloaded again; otherwise it won’t work
It has passed the self-check, so that means this new spare part is good, right?