I hope an expert can help resolve some doubts I have regarding RS flip-flops in the interlock logic diagrams of SIS systems

2017-07-31View Original

Thread Content

The last edit to this post was made by sb5436 on 2017-7-31 at 10:08. 1. Why is a NAND gate used at the S input of the RS flip-flop in Figure 1 compared to Figure 2? Won’t the value at the S input become 0 after using a NAND gate?; ②What does the small circle in front of the OR gate’s input mean? ; ③Why do both Figure 1 and Figure 2 use the Q non-terminal output? Doesn’t the textbook state that it should be the Q terminal output? 2. Can Figure 2 be understood in this way: when the trigger terminal S is 1, the output terminal is immediately set to 1; thereafter, regardless of the state of S, the output terminal remains at 1 until the flip-flop is reset, that is, when the reset terminal R becomes 1, at which point the output terminal changes to 0 and remains there until S resets the flip-flop again? 3. In university electrical engineering, I learned about the two basic RS flip-flops composed of NAND and NOR gates. When using them in practice, I found that they differ significantly from the RS flip-flops used in SIS systems; this caused me a lot of confusion. I hope for some guidance!
Reply #22017-07-31
This post was last edited by superme84 on 2017-7-31 at 12:30. Electrical engineering in universities is taught using positive logic, whereas this SIS employs negative logic for programming and configuration; both inputs and outputs use \"fail-safe contacts\", meaning a value of 0 indicates operation, while 1 indicates maintenance of the current state. Points to note: 1. For the input – low pressure in the main gas pipeline, the trigger value is 0 rather than 1; therefore, an inversion operation is required to activate the RS flip-flop. 2. What does adding a small circle mean? It means inverting the signal; since the reset button triggers an action of type 1, inversion is used to ensure consistency with the logic related to low pressure. 3. The output is a 0 action, so the Q non-terminal output is used.
Reply #32017-08-01
The answer above is correct; the main difference in the logic between SIS and DCS is that in SIS, 0 represents a valid value, while in DCS, 1 represents a valid value. The most significant consequence of this difference is that, when there is a power outage, the output signal from SIS becomes all 0s, as there is no power available. As a result, all the necessary actions are taken, ensuring absolute safety in fault conditions. In contrast, with DCS, the signal is 0 when power is lost, and everything remains in a non-active state, thereby ensuring continuous production
Reply #42017-08-02
In the SIS safety interlock system, elements such as the low-low pressure button and the bypass circuit are always under voltage. For example, when a low-low alarm occurs, the value becomes 0; subsequently, NOT becomes 1, causing the RS flip-flop to be set to 1. When the low-low condition is no longer present, pressing the reset button changes the value to 0, and after inversion it becomes 1. I’m a bit confused here – I think the inverted signal from the reset button should be connected directly to the RS flip-flop, rather than going through an OR operation followed by inversion before being connected to the RS flip-flop
Reply #52017-08-02
Take a close look at the interlock logic diagram and you’ll understand.
Reply #62022-05-05
Is the reset button normally 0, and becomes 1 when pressed?
Reply #72022-06-05
I would like to ask about the interlock logic relationships on the chemical operator page. And/or: An action is taken only when all two or more conditions are met. . Or, for two or more conditions, an action is taken as long as one of them is met. Is this the correct way to understand it? ? (Why did my colleague say I got it wrong?)
Reply #82022-06-05
This post was last edited by jlshnlhj on 2022-6-5 18:56 with the caption: “Action is taken only when all conditions are met.” Saying “action” is inaccurate. Negative logic is incorrect, and it’s reversed as well. Generally, it’s all 1, with 1 appearing. Whether it’s positive or negative logic. As for whether it’s a 0 or a 1 action, that’s another matter.

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.