2017-08-20View Original

Thread Content

Question: In the AIN module of I/A, there is a parameter called HLDB, which seems to be the high-limit deadband. There are several questions: 1. If I set this value to 1, does it refer to 1% of the range or 1 unit? 2. With this parameter set, how does the overreporting to the maximum value work? Thank you.
Reply #22017-08-21
1. If I set it to 1 here, does it refer to 1% of the range or 1 unit? It’s not a percentage, but a unit value. 2. With this parameter set, how does the overreporting to the maximum value work? The dead zone is designed to function when the alarm returns to normal. For example, if HLDB is set to 5, the high alarm value is 80. So, set the alarm at 80, and wait until the AIN output reaches

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.