This post was last edited by tiandiyi*an on 2017-9-8 07:16. I encountered Melsungen SV-Ⅱ positioners on site; in two of those positioners, only the pressure gauge at the inlet side had pressure, while no compressed air came out from the outlet side, even though there should have been signal output. The pressure gauge on the exhaust port also shows no pressure. What’s going on? There is also another locator for which the inlet and outlet ports have no pressure; the pressure readings are normal, and the pressure reducing filter is also in good condition. The positioner main board is also good.
Reply #22017-09-08
The first possible cause is that the constant orifice of the regulator is blocked, resulting in no air output~~ What is the quality of your instrument air? The second issue is that there seems to be no instrument air at all; check the instrument air supply~~

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.