No signal when pulse signal is sent to the deltav multi-functional card

2017-09-26View Original

Thread Content

It’s a field-mounted dual-rotor flow meter, three-wire type; pulses are sent to a multi-functional card, but the card fails to detect signals. How should this be configured?
Reply #22017-09-27
In the channel properties, enable the channel, and then select pulse input channel as the channel type. Sometimes it is also necessary to adjust the filter; it’s best to use a signal generator to generate pulse signals, fine-tune the DCS side first, and then connect it to the field
Reply #32017-09-27
Should it be frequency or pulses? The frequency is displayed in the studio, but the signal from the field cannot be read
Reply #42017-09-27
There is a control there for setting the cycle period; the default value seems to be 1.3s
Reply #52017-09-28
Then adjust the flow meter on-site to check whether a pulse signal is being output.

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.