Why is the remote transmitted current signal of a metal tube float flow meter higher than the on-site indication?

2017-10-02View Original

Thread Content

For a gas flow meter with a capacity of 200 cubic meters, the on-site reading shows 80 cubic meters, while the current signal indicates 11 mA (in a 4-20 mA range). What could be the reason for this?
Reply #22017-10-02
The mechanical zero (range) of the flow meter does not match the remote zero (range).
Reply #32017-10-03
First, set the float and pointer to zero, and check whether the output is 4mA

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.