HCBBS Forum (English)
Submit Chemical Projects / Find Solutions
Amplify Your Requirements on a Broader Chemical Platform *Engineering · Technology · Equipment · Solutions*
Submit Request

Regarding when to use thermistors and when to use thermal resistors

2017-10-19View Original

Thread Content

There is a significant difference between temperature transmitters that use 4-20mA signals and thermal resistors that use PT100 signals; the cost difference for DCS cards is also substantial. For design institutes, how should they make choices during the design process? Are there any guidelines?
Reply #22017-10-19
The current regulations do not provide any provisions.
Reply #32017-10-19
The current regulations do not provide any provisions.
Reply #42017-10-19
If the working environment on-site allows temperature variations within the range of -50 to 70 degrees, it is possible to use it there; however, in case the working conditions are harsh, it is better to use a card-type device to avoid failures caused by such conditions. I’ve also used both of the methods you mentioned, and the failure rate of the card components is significantly lower.
Reply #52017-10-19
One advantage of temperature variation is that it can provide isolation, protecting the card components. For future maintenance and management, if I can use current signal cards to measure temperature. Then I can save a lot of costs. There’s no need to have too many different types of card inserts. If on-site temperature variation is not required, I can also use a temperature safety barrier to achieve the function of temperature variation. For ordinary thermal resistors, the error of thermocouples shall not exceed ±1.0°C. The accuracy of the D/A converter is ±0.025% of full scale, with good cold-end compensation; the overall temperature effect is ±0.1%/28°C. Therefore, in special operating conditions where high precision with regard to temperature is required, a temperature-compensated version must be used.
Reply #62017-10-19
For on-site signals that need to be isolated or transmitted over long distances, thermistors should be used; for others, thermal resistors can be considered.
Reply #72017-10-23
I am here to learn*. Our devices also have thermal resistors and thermocouples; I can’t tell the difference between them
Reply #82017-10-23
The control circuit uses temperature sensing; an integrated or separate type can be chosen depending on the ambient temperature
Reply #92017-10-23
1. If you don’t want different types of DCS card backups, temperature compensation can be used; however, the cost is not as low as mentioned above – on the contrary, it is higher. 2. The accuracy generally decreases when temperature compensation is used. 3. If there are few temperature points, it is recommended to use a temperature-sensitive element; if there are many points, either option is acceptable. 4. If lightning protection and isolation are considered necessary, use a temperature-sensitive element. 5. When using a temperature-sensitive element, make sure to choose one of good quality, otherwise you won’t even be aware of temperature drift. One thing to note: domestic temperature-sensitive elements tend to experience significant drift after a few years of use, which is far worse than using DCS temperature card terminals.
Reply #102017-10-23
First, Party A requires that we normally opt for an integrated temperature sensor; for smaller factories, a Pt100 will suffice to meet the requirements. I recommend choosing an integrated temperature sensor

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.