Rosemount vortex flow meter

2017-11-09View Original

Thread Content

No response was observed after the valve was opened, and the flow rate did not change. After the valve is closed, there is still 10 percent flow rate.
Reply #22017-11-09
Re-calibrate the zero point after confirming that the valve is closed. Check if the pipeline is vibrating.
Reply #32017-11-09
1 Remove the flow meter and place it on the ground to check whether it returns to zero, and see if there is any material stuck on the vortex generator. 2 The parameter settings must be correct; otherwise, the traffic indicator will show abnormal values. 3 The on-site installation is quite messy; instrument management needs to be improved.
Reply #42017-11-09
It was zero when it was removed. My medium is oxygen
Reply #52017-11-09
Low-pass filtering, or low-flow rejection
Reply #62017-11-09
Even after the valve is closed, the indication is still caused by vibration; the flow rate remains unchanged when the valve is opened, which suggests that the settings aren’t correct. Please read the manual carefully.
Reply #72017-11-11
Installation issue: the flow meter is not firmly fixed, resulting in errors caused by vibration.
Reply #82017-11-12
Rosemount’s vortex flowmeters do not require zero calibration.

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.