The valve vibrates severely; how to deal with it?

2017-12-07View Original

Thread Content

As shown in the figure, the PV1001 pressure regulating valve is a diaphragm air-operated valve of the flow-on type, with a DN25 size. The valve stem vibrates significantly; the vibration of the valve body is acceptable. I consulted the manufacturer, and they said it’s not possible to create a cage-type sleeve valve of such a small size. Is it possible to make adjustments from a technical standpoint? F1-F5 are manual valves, with F1 and F2 being normally closed.
Reply #22017-12-07
Supports were added before and after the valve, but with little effect
Reply #32017-12-07
Supports were added before and after the valve, but with little effect
Reply #42017-12-08
If the flow rate is acceptable, can we secure the manual valves before and after the pneumatic valve? ①One is fine too
Reply #52017-12-08
If the flow rate is acceptable, can we secure the manual valves before and after the pneumatic valve? ①One is fine too
Reply #62017-12-08
Are all the supports working? In some areas, the support is merely for show; it’s only a few centimeters above the ground~~~
Reply #72017-12-08
Try adding a small buffer cylinder behind the valve. Ensure that there are no large fluctuations in gas supply for users.
Reply #82017-12-08
It’s caused by an excessive pressure difference before and after the valve; The bypass valve can be slightly opened, while the upstream valve should be closed ; Or add a flow-limiting orifice plate between the upstream valve and the control valve.
Reply #92017-12-08
Or try using a different thin film tip
Reply #102017-12-08
If fixed and support issues are excluded, the likely causes are: 1. The pressure difference before and after the valve is too large; 2. The flow rate is significantly below the designed value, with the valve opening being less than 20%; 3. This is likely a case of pressure self-regulation – the pressure measurement point should be located close to the control valve. If there is a buffer tank in the downstream system, the measurement can be taken at that tank; otherwise, it should be taken at a location further away from the control valve. In the case of the first two situations, the manual valve located after the control valve can be gradually closed down until the vibration is reduced to an acceptable level and the pressure regulation curve becomes satisfactory. In the case of the third scenario, it is estimated that the control valve will operate frequently, with significant changes in its opening degree; vibrations will also vary accordingly. If no buffer tank is available, a section of large-diameter pipe should be added to the pipeline downstream of the valve (functioning as a buffer tank), and pressure readings should be taken from this pipe.

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.