HCBBS Forum (English)
Submit Chemical Projects / Find Solutions
Amplify Your Requirements on a Broader Chemical Platform *Engineering · Technology · Equipment · Solutions*
Submit Request

Frequent disconnection of analog data in Siemens PLC 485 communication

2018-01-06View Original

Thread Content

The model is S7-200 226 series; it has 3 additional digital input modules and 4 additional analog input modules. When no analog input modules are connected, the 485 communication is carried out using the MODSCAN332 device. The digital inputs and outputs work properly, while all analog inputs show a value of 0, with no loss of connection. Once the analog input modules are connected, the digital inputs and outputs still function properly without any loss of connection. There are 16 analog inputs in total; the first 3 and the last 3 do not experience any loss of connection, while those in the middle lose connection frequently. The digital inputs, on the other hand, remain stable with no loss of connection. What’s the solution? ? ? ? ? ? ? ? ? ? ? ? ? The PLC suspects that the port is damaged; after replacing it with a new one, the same problem persists. The grounding has also been checked
Reply #22018-01-08
Try reducing the communication baud rate.
Reply #32018-01-08
I remember that Siemens has a module for cyclic scanning; let’s see if there is a functional module that allows automatic connection after cyclic scanning: lol
Reply #42018-01-08
This post was last edited by huio1983 on 2018-1-8 09:15; 485 communication requires terminal resistors
Reply #52018-01-08
Simpi, that Nazi dog’s cousin – he deserves to be sick! . :P. . . . . . Brother doesn’t want to tell you where the disease is. My brother is here to enjoy the scenery :lol .
Reply #62018-01-16
The Lenovo ThinkPad I used didn’t work for testing; I tried an Acer laptop instead, and the data was stable. Why is that? ? ? ? ?

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.