Voltage issues after passing through the MTL ICC212 isolator

2018-01-18View Original

Thread Content

The output voltage of the ICC212 isolator became 27V in all cases; although this does not affect the data, it prevents the 475 from being connected. Power supply: the voltage output by the card is 24V, which is normal. These past few days, everything has suddenly changed to 27V; I can’t figure out the reason. I’m seeking advice from experts. Or provide the MTL technical support phone number
Reply #22018-01-18
Also concerned about this issue; I hope the original poster can share their solutions
Reply #32018-01-18
The power supply should be divided into different sources, I guess. Check the power supply used for output
Reply #42018-01-18
Suggestion: Disconnect from the field instruments and measure the output voltage of the safety barrier to check whether it is 24V, in order to determine whether the issue lies within the system or outside of it. Personally, I think it might be due to poor grounding. Pay attention
Reply #52018-01-19
I agree with the view from the seventh floor: first disconnect the connection to the field, and measure the output voltage. If the voltage is fine, then there is a problem with the wiring or the meter; if the voltage remains at 27V, it is recommended to try using a different safety gate
Reply #62018-01-24
Check to see if there is a short circuit between the positive and negative terminals, and inspect the wires

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.