Regarding the resistance value of the thermal resistor and the display issue in the DCS

2018-05-05View Original

Thread Content

It’s now the Endress+Hauser system; the thermal resistors on site are located in the cabinet room. The resistance values for A and B are over 130 ohms, while those for A and C are 7 ohms. However, the temperature displayed by the DCS shows negative values. Other temperatures displayed correctly when connected to this channel. Everyone, please analyze what the reasons are
Reply #22018-05-05
Lines A/B/C might be connected incorrectly; also, consider the possibility of the wires being connected to the casing.
Reply #32018-05-05
Check the wiring or replace the thermistor.
Reply #42018-05-05
Disconnect the circuit at the site and measure the thermistor; if the thermistor is fine, then it’s a problem with the external circuit
Reply #52018-05-05
If other temperatures are displayed correctly on this channel, on-site issues should be considered. Swap the on-site thermal resistor to another channel to see if it still reads a negative value.
Reply #62018-05-06
For the other channels connected to the same card, as well as those connected to other good cards, if the value is 130 ohms then there’s no problem on site; check the three-wire and four-wire settings for those channels, along with the wiring.
Reply #72018-05-06
The signal line should be connected in series with the voltage. Either there is potential interference. Also, B and C7Ω are a bit too high
Reply #82018-05-06
Measure the voltage of the wire; short-circuit one end to measure the resistance of the wire

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.