I ran into a strange problem today: the control valves on the DCS show normal readings, but the display on the positioners isn’t lit, and the control valves won’t move

2018-11-22View Original

Thread Content

To be more specific, after disconnecting the ± terminals after trading hours, the measured voltage was 24 volts. The positive terminal has no connection to ground, the negative terminal also has no connection to ground; the wires used for calibration are from this same set. The measured current is 50% of 12 mA, which matches the expected values. However, when the ± terminals are connected together, without a safety barrier in place, the measured voltage is only 0.9 V. The other AO points, when connected to control valve loads, show a normal voltage of 10 V. It is the low voltage of 0.9 V that prevents the actuator from functioning. I forgot to ask whether the voltage was measured with the wires disconnected at the site! ! ! ! What is the reason? ? ?
Reply #22018-11-22
Is the locator broken? How about trying a different locator?
Reply #32018-11-23
It’s most likely a fault with the locator, along with an excessively high load resistance, which causes a significant voltage drop
Reply #42018-11-23
Measure the voltage at the site; there might be a problem with the wiring there. Generally, if the voltage at the site is below 12V, the smart locator will not operate stably
Reply #52018-11-23
There must be some poor contacts in the cable; measure the resistance of the wire
Reply #62018-11-23
Here, it works properly when the voltage is reduced to 10V
Reply #72018-11-24
How long is the line? Is it over 500 meters?
Reply #82018-11-24
Check whether the cable is damaged, or try using another cable of the same type or a safety barrier to see if the load is insufficient

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.