2018-12-25View Original

Thread Content

Dear seniors at HaiChuan, while reading today I came across a passage that I don’t quite understand; I hope you can help me figure it out. In terms of flow measurement, **the standard specifies that the flow ratio applicable to throttle devices is 30% (maximum flow: minimum flow = 1:3). This is because the differential pressure is proportional to the square of the flow rate, and accuracy cannot be guaranteed when the flow ratio is below 30%. Furthermore, when the flow rate is less than 30%, the Reynolds number is often below the critical Reynolds number, and the flow coefficient is not constant, resulting in inaccurate flow measurement. The two sentences that are not understood are: 1. What does it mean when the traffic ratio is below 30%? 2. When the flow rate is below 30%, does this refer to 30% of the maximum flow rate of the throttling element or 30% of the actual flow rate in the current operation? Please explain
Reply #22018-12-25
Range ratio, minimum flow: maximum flow. The common range ratios are 1:3 and 1:4.
Reply #32018-12-25
Answer: The “maximum flow rate” mentioned here refers to the rated maximum flow rate of the throttle element, that is, the nominal flow rate, which is a constant value.
Reply #42018-12-25
In differential pressure flow calculation, it is necessary to provide the values for rated flow, maximum flow, typical flow, and minimum flow. The 30% mentioned in the standard refers to 30% of the rated flow rate ; A value below 30% means that at low flow rates, the Reynolds number does not reach the turbulent regime; changes in the Reynolds number lead to changes in the discharge coefficient, which in turn means a deviation from the values provided by the initial calculations, and as a result the required measurement accuracy is not achieved. Therefore, flow measurement has range requirements.
Reply #52018-12-25
I see. It’s a pity that our throttle element specification sheet only lists the operational flow rate and the maximum flow rate of the orifice plate
Reply #62019-04-24
1/When the flow ratio is below 30%: Maximum flow: Minimum flow = Flow ratio. 2. When the flow rate is below 30%, this refers to being below 30% of the maximum flow rate, not 30% of the actual flow rate used in the process operation

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.